Advances in DER Interconnection Processes and Study Methods1
Advances in DER Interconnection Processes and Study MethodsAlex Nassif, Specialist Engineer
Advances in DER Interconnection Processes and Study Methods
EVOLVING DER ENVIRONMENT IN ALBERTA
• Significant rise in interest for DER connections circa 2014
• Punitive rules incented gas-fired DERs
• Incentives introduced for low-emission commercial and load offsetting installations
• Two categories for DER in Alberta with different requirements:
1. Micro-Generation (MG)
2. Distributed Generation (DG)
2
2018-05-08
2
Advances in DER Interconnection Processes and Study Methods
DISTRIBUTION SYSTEM CONNECTION CONSIDERATIONS
Distributed Energy Resources – Why connect to the D-System?
1. Fit for purpose
2. Lower connection cost
3. Faster interconnection process
3
Advances in DER Interconnection Processes and Study Methods
DISTRIBUTION SYSTEM CONNECTION CONSIDERATIONS
Considerations
1. ATCO system serves predominantly industrial load with low customer density and long feeders
2. 25kV feeders may accommodate up to 25MW
• Maximum standard line apparatus rating of 600A
• In-line devices and conductors with gradually reduced rating
3. Anti-Islanding protection required
• Safety and technical liability concerns
• Transfer Trip is the standard solution for synchronous generators
• Will accept IEEE 1547, UL-1741-SA and CAISO Rule 21 approved inverters
4
2018-05-08
3
Advances in DER Interconnection Processes and Study Methods
DISTRIBUTION SYSTEM CONNECTION CONSIDERATIONS
4. DERs are not permitted to actively regulate voltage on distribution networks in Alberta. (Not Yet)
5. Voltage management is more difficult with distance from the Substation
• R/X characteristics – voltage rise issues
• VAR control becomes less effective
5
Distribution Line
VS VR
Substation PL+jQL
R+jX
DG
PG+jQG
PX
RQ
S
GLGLRS
V
XQQRPPVVV
Advances in DER Interconnection Processes and Study Methods
BECOMING A DER ENABLER
Recent Enabling Developments:
1. Introduced a DG preliminary assessment (Free of Charge)
2. Streamlined DG distribution system study requirements
3. Created and published enhanced information for developers and utility staff (DG & MG primers)
6
2018-05-08
4
Advances in DER Interconnection Processes and Study Methods
BECOMING A DER ENABLER
4. Hosting Capacity (HC) for MGs
• Conducted R&D methods to determine HC
• Releasing Capacity Maps
5. Investigated alternatives for DGs TT:
• Inverters active anti-islanding protection
• Passive anti-islanding protection (addressed later in this presentation)
• Power Line Carrier alternative
7
Advances in DER Interconnection Processes and Study Methods
BECOMING A DER ENABLER
6. Developing Grid Modernization Strategies to enable an interactive environment:
• Advanced Distribution Management System (ADMS).
• Advanced Metering Infrastructure (AMI)
• DER Management Systems (DERMS)
8
2018-05-08
5
Advances in DER Interconnection Processes and Study Methods
DG INTERCONNECTION PROCESS
To meet developer expectations and manage manpower commitment, a streamlined DG interconnection process was developed:
1. Preliminary Planning Assessment – 1 week
2. Feasibility Assessment (Application for Connection) – 30 days
3. Connection Proposal (Acceptance of Feasibility Assessment)
4. Engineering Design, Construction and Commissioning (Project Acceptance)
At each step all costs are borne by the customer alone
9
Advances in DER Interconnection Processes and Study Methods
DG INTERCONNECTION PROCESS
1. Phase 0 - Preliminary Planning Assessment (optional)
• ~ 1 hour of planner’s time
• High level connection feasibility assessment based on engineering judgement
• Utilize • GIS
• Distribution Switching Maps
• Substation SLDs and Load Forecasts
• Free of charge
10
2018-05-08
6
Advances in DER Interconnection Processes and Study Methods
DG INTERCONNECTION PROCESS
2. Phase 1 - Feasibility Assessment• Distribution study covering steady-state as well as DG &
load rejection conditions.• Determine feasible generation connection limits,
including specified operating power factor with and without upgrades to the distribution network.
• Ballpark scope for distribution connection and transmission requirements (DTT & substation logic)
• OOM estimate (T & D) provided by Project Manager• Requires an application fee
11
Advances in DER Interconnection Processes and Study Methods
DG INTERCONNECTION PROCESS
3. Phase 2 - Connection Proposal
• Site visit and firm estimate from Distribution
• Dynamic studies (if required) using an EMTP
• DBM scope and estimate from Transmission
• Firm connection proposal provided to DG developer
• A fee is collected. If project does not proceed, unspent monies are returned to the DG developer.
12
2018-05-08
7
Advances in DER Interconnection Processes and Study Methods
DG INTERCONNECTION PROCESS
4. Engineering Design, Construction and Commissioning
• Moves to project execution and is no longer in the planning realm
13
Advances in DER Interconnection Processes and Study Methods
EUA: MICRO-GENERATION (MG) REGULATION
• Not to exceed annual load consumption
• Not to exceed the Electric service
• Renewable or Alternative (Emissions < 418kg/MWh)
• Small MG < 150kW, Large MG > 150kW
New enabling conditions:
• Annual load offsetting (multiple adjacent metered sites allowed)
• Nameplate up to 5MW (from previous 1 MW limit)
14
2018-05-08
8
Advances in DER Interconnection Processes and Study Methods
MG INTERCONNECTION PROCESS
MG Process:1. Application filed with the DFO
2. Meets renewable/alternative requirements
3. Commercial eligibility (load offsetting)
4. Technical assessment
5. Bi-directional meter installed by DFO
Predicated on system upgrades not being required – DFO bears connection cost
15
Advances in DER Interconnection Processes and Study Methods
MG INTERCONNECTION PROCESS
ATCO recent enabling activities:
• Updating the MG connection process
• Developed an MG connection primer for staff use
• Developed hosting capacity guidelines and algorithms
• Developed Technical Interconnection Requirements for DERs that must be met by both MGs and DGs
16
2018-05-08
9
Advances in DER Interconnection Processes and Study Methods
TRANSITIONING FROM ACCOMMODATING INTO COOPERATING
Increasing Hosting Capacity and Improving Grid Reliability
ATCO is leveraging smart inverter technologies, by aligning its Technical Interconnection Requirements with those of revised versions of IEEE 1547 and UL 1741:
• Autonomous control functions (e.g., Volt-VAR, Volt-Watt)
• Remote control functions (e.g., dynamic PF, VAR and/or Watt output)
• Enhanced disturbance ride through for system level contingencies
• Visibility and controllability
• Anti-Islanding Protection
Investigating telecom requirements and options
17
Advances in DER Interconnection Processes and Study Methods
UPDATES ON DER INTERCONNECTION STANDARDS
1. UL 1741 SA released September 2016
• Includes performance functions as per CAISO Rule 21
2. IEEE 1547 released April 2018
• Aligned with CAISO Rule 21 and UL 1741 SA
3. CSA C22.2 No. 257 (inverters) and CSA C22.3 No. 09 (DERs) to be consolidated and aligned with UL and IEEE standards
ATCO, Fortis and ENMAX are part of CSA Task Forces
18
2018-05-08
10
Advances in DER Interconnection Processes and Study Methods
TECHNICAL INVESTIGATIONS/INNOVATION
1. Mitigating overvoltage caused by DERs
2. 8760 Planning for PVs
3. Application of passive protection schemes in selected cases
4. Measures to reduce protection miscoordination
19
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Problem Definition
20
Distribution Line
VS VR
Substation PL+jQL
R+jX
DG
PG+jQG
PX
RQ
S
GLGLRS
V
XQQRPPVVV
This work was presented in: A. Nassif, X. Long, “Mitigating Overvoltage Scenarios Caused by Large Penetration of Distributed Energy Resources”, 2016 IEEE Electrical Power and Energy Conference, October 12-14, 2016.
• DERs must operate under PF control
• Active power flow causes voltage rise
• PCC voltage is higher under light loading
• R/X characteristics – voltage rise issues
• VAR control is less effective
2018-05-08
11
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Voltage regulator-based solution:
• Neutral Idle (preferred)
• Co-Gen: Reverse settings required
32-step tap changers that provide ±10% regulation
21
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Power Factor-based solution is limited:I. PF range for inverters is often ± 90%
II. Synchronous gens: capacity curve – often +90% to -0.97% @ rated
III. Induction gens: usually around -89% when not coupled with inverter
22
2018-05-08
12
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Circuit-based solution: Reconductor the distribution line
• Reduction of the equivalent thevenin impedance at PCC
Expensive!
23
1.025
1.030
1.035
1.040
1.045
1.050
1.055
1.060
1.065
1.070
0 5 10 15 20 25
Vo
ltag
e P
rofi
le [
p.u
.]
Distance to Substation [km]
Pf = -0.95
Reconductor
Conductor R (Ω/km) X (Ω/km) B (uS/km)
1/0 0.55 0.46 3.80
#266 0.22 0.40 4.13
#477 0.12 0.38 4.41
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Distribution STATCOM – manages voltage through VAR exchange
• DFO manages VAR exchange
24
1.030
1.035
1.040
1.045
1.050
1.055
1.060
1.065
1.070
0 5 10 15 20 25
Vo
ltag
e P
rofi
le [
p.u
.]
Distance to Substation [km]
PF = -0.95
STATCOM
2018-05-08
13
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Change the DER operating mode voltage control (DER controls voltage):
• Autonomous Volt-VAR control mode
I. Limited effect
II. Difficult to coordinate with the utility
• Autonomous Volt-Watt control mode
I. Very effective
II. Essentially local power curtailment
III. Difficult to coordinate with the utility
25
Advances in DER Interconnection Processes and Study Methods
MITIGATING OVERVOLTAGE CAUSED BY DERS
Future Direction: Coordinated Control (DERMS)
• Coordinate operation between the utility and the DER.
• A system similar to EMS.
• DFO will be able to send signals to control DER output, PF, control modes, etc.
26
2018-05-08
14
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING – INCREASING CONNECTION SIZE
• 15 MW PV DER application (1st in queue)
• 5 MW synchronous DER application for 5MW (2nd)
• 12.9 MW POD Capacity
• Minimum POD loading (excluding outages) considered
• Traditional planning:
• Limit PV DER @ 12.9 MW
• Reject Synchronous DER
27
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING – INCREASING CONNECTION SIZE
Load Duration Study
28
Case 1 Case 2 Case 1 Case 2
# of kWh curtailed* 27148 26932
# of hours curtailment
occurs* 25 22
% of kWh curtailed* 0 0
% of hours curtailment
occurs* 0 0
*assuming synchronous DER operates at 5MW production 8760
Case 1: PV @ 13.3 MW and tilt angle 45 degreesCase 2: PV @ 13.3 MW and tilt angle 52.8 (optimum) degrees
2018-05-08
15
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING - SMART INVERTERS AND BESS
29
Re
acti
ve P
ow
er
Ab
sorp
tio
nIn
ject
ion
VL V1 V2 VRef V3 V4 VH
Dead Band
Act
ive
Po
wer
Ou
tpu
t
VL VRef VH
Dead Band
This work will be published in: A. Nassif, T. Greenwood-Madsen, S. Pirooz-Azad, D. Teshome, “Feeder Voltage Management through Smart Inverter Advanced Functions and Battery Energy Storage System”, 2018 IEEE PES General Meeting, (accepted – August 2018)
Autonomous Voltage Control Inverter Functions
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING - SMART INVERTERS AND BESS
Hypothetical scenario: a feeder in Fort McMurray with 50% penetration distributed PV
30
VS
0.6 km
PV
Distributed 1ph and 3ph loads
7 km
#1 AL
PVPVPVPVPV
Distributed 1ph and 3ph PV
0 100 200 300 400 500 600 700 8000
100
200
300
400
500
PV
outp
ut
[kW
]
Volt-Watt
PF=1
0 100 200 300 400 500 600 700 8000
500
1000
1500
PV
outp
ut
[kW
]
Hour
Volt-Watt
PF=1
Last PV
First PV
0 100 200 300 400 500 600 700 8001.02
1.04
1.06
1.08
1.1
1.12
EO
L V
oltage [
p.u
.]
Volt-Watt
PF=1
0 100 200 300 400 500 600 700 8001.03
1.035
1.04
1.045
1.05
1.055
BO
L V
oltage [
p.u
.]
Hour
Volt-Watt
PF=1
About 23% of energy curtailed in June.
Less than 10% curtailment for the full year.
2018-05-08
16
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING - SMART INVERTERS AND BESS
BESS effect: Best siting:
31
0 100 200 300 400 500 600 700 8001.02
1.04
1.06
1.08
1.1
1.12
EO
L V
oltage [
p.u
.]
Volt-Watt
PF=1
BESS 1MWh
BESS 5MWh
BESS 7MWh
0 100 200 300 400 500 600 700 8001.02
1.04
1.06
1.08
1.1
BO
L V
oltage [
p.u
.]
Hour
BESS 1MWh
BESS 5MWh
BESS 7MWh
A 7MWh BESS would be required to keep voltages within targets as compared to Volt-Watt.
0 1 2 3 4 5 6 7 81
1.01
1.02
1.03
1.04
1.05
Voltage [
p.u
.]
Distance from Substation [km]
Advances in DER Interconnection Processes and Study Methods
8760 PLANNING - SMART INVERTERS AND BESS
• Volt-VAR is not effective
• Volt-Watt is very effective and economical (to DFO)
• BESS levels off renewable production, but is expensive
• DERMS is a global solution that retains control to DFO
32
Solution Cost Advantages Limitations
Advanced Inverter Functions
LowEffective, localized
solution (Volt-Watt).
Removes utility control. Curtails inverter output.
DERMS Very HighGlobal solution.
Does not remove utility control.
Curtails inverter output, but optimally.
BESS HighUtility retains
control. Provides ancillary services.
Complexity.
2018-05-08
17
Advances in DER Interconnection Processes and Study Methods
ANTI-ISLANDING PROTECTION SCHEMES
Islanding:
• Operational and Safety concerns
• Detection and extinction in less than 2 seconds (as per IEEE 1547 and CSA C22.3 No 9 & C22.2 No 257)
• Current methods to industry today:1. Telecom-based
2. Active protection
3. Passive protection
33
This work was published in: A. Nassif, C. Madsen, “A Real Case Application of ROCOF and Vector Surge Relays for Anti-Islanding Protection of Distributed Energy Resources”, 2017 IEEE Electrical Power and Energy Conference, October 22-25, 2017
Advances in DER Interconnection Processes and Study Methods
ANTI-ISLANDING PROTECTION SCHEMES
Telecommunication-based (DTT) – standard solution
• Most dependable and secure scheme
• Operates under breaker/dry contact open/close status
• Telecom fail safe provision
• Does not have Non-Detection Zones (NDZ)
• Often the most expensive
34
2018-05-08
18
Advances in DER Interconnection Processes and Study Methods
ANTI-ISLANDING PROTECTION SCHEMES
Active schemes
• Active frequency drift (Sandia)
• Positive feedback
• Negative feedback
• Reactive current injection
• Native to most modern inverter technologies
• Difficult to implement in an external relay
35
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
Passive schemes
• Under/Overvoltage (27, 59), under/over frequency (81)
• Vector Surge (78) and Rate-Of-Change-Of-Frequency (ROCOF - 81R)
• All of them have NDZs
• The more dependable, the smaller the NDZ
• The more secure, the larger the NDZ
36
2018-05-08
19
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
Synchronous Generators
1. Predict the rate of frequency change
2. Predict the angular surge
3. Determine the relay detection speed
37
PH
f
dt
dfP
Hdt
d
22
00
H – inertia constant (s)ΔP – power mismatch (p.u.)
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
ROCOF and Vector Surge relay detection times
38
0
0.1
0.2
0.3
0.4
0.5
0.6
0.7
0.8
0.9
1
0 0.2 0.4 0.6 0.8 1
Trip
pin
g T
ime
(s)
Power Imbalance (pu)
H = 2 s
alpha = 20
alpha = 10
alpha = 8
alpha = 5
alpha = 2
2018-05-08
20
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
Case study: interim connection
• DTT would involve a T-Tap POD, plus two terminal PODs.
• DTT timeline would strain the project feasibility.
39
VS
0.6 km
DER
ACSR 266
8 km
ACSR 1/0
5 km
ACSR 1/0
9 km
ACSR 266
PCC
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
• Loading Scenarios :
• Summer Min load 7.6 MW, max DER export 6.25 MW (ΔP = 0.22 p.u.)
• Winter Min Load 8.1 MW, max DER export 6.9 MW (ΔP = 0.18 p.u.)
• A reverse power relay (32) was used to guarantee these conditions
40
2018-05-08
21
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
Outcomes:
• The DG remained in operation and protected by the ROCOF alone for 2 years
• No nuisance trips
• Operated when required
41
Advances in DER Interconnection Processes and Study Methods
PASSIVE ANTI-ISLANDING PROTECTION SCHEMES
Lessons learned:
• Passive protection may be used for synchronous generators under favorable scenarios
• Considered on a case-by-case basis (study required)
• For inverters, this element will not work well:
• Lack of inertia means large but fast change in frequency
• Load (rather than generator) inertia plays a large role
42
2018-05-08
22
Advances in DER Interconnection Processes and Study Methods
FEEDER PROTECTION DE-SENSITIZATION
DER Infeed causes feeder de-sensitization:
43
Substation
F0.07s 1s 5min
DG
Substation
Portion of line unprotected
until DG trips
F0.07s 1s 5min
VS
VGZL1 ZL2
IS_F
F
IG_F
Positive-sequence
Zero-sequence
VS_0
VG_0ZL1_0 ZL2_0
IS_F0
ZG_0
ZS_0
V0
IG_F0
ZL_0IL_F0
This work was published in: A. Nassif, “An Analytical Assessment of Feeder Overcurrent Protection with Large Penetration of Distributed Energy Resources”, IEEE Transactions on Industry Applications, 2018 (early access)
Advances in DER Interconnection Processes and Study Methods
FEEDER PROTECTION DE-SENSITIZATION
Case Study:
• DER will de-sensitize the upstream protection
44
Substation
36km
2km
16km
DG – 5MW/7MWType of fault Location No DER 5MW 7MW
LLL
Sub 406 297 278
DER - 342 393
EOL 406 620 653
Bolted LG
Sub 247 170 157
DER - 312 338
EOL 247 475 488
20ohm LG
Sub 207 119 108
DER - 217 232
EOL 207 330 336
2018-05-08
23
Advances in DER Interconnection Processes and Study Methods
FEEDER PROTECTION DE-SENSITIZATION
Solutions and Limitations:1. Increase sensitivity of feeder relay – may not be possible
2. Change DER location – fuel source dependent
3. Implement distance protection – similar issue through different angle
4. Sectionalize the feeder – additional interrupter
5. Change transformer winding connection – only effective for I0
6. Accept sequential tripping – will extend fault clearing time
45
Advances in DER Interconnection Processes and Study Methods
FUTURE DIRECTION
• Ongoing enablement of DERs requires a paradigm shift for both DFOs and DER owners/operators
• Coordinated operations will be imperative and will require expanded data collection, telemetry, control and functionality
• DFOs will leverage DER advanced functions to improve the system performance and increase penetration
• It is cooperation rather than tolerance