CP001D/06/en/03.10 71024143 INDD CS2 Flow measurement Selection guide Instruments International Endress+Hauser Instruments International AG Kaegenstrasse 2 4153 Reinach Switzerland Tel. +41 61 715 81 00 Fax +41 61 715 25 00 http://www.endress.com [email protected]
Transcript

CP001D/06/en/03.1071024143INDD CS2

Flow measurementSelection guide

Instruments International

Endress+HauserInstruments International AGKaegenstrasse 24153 ReinachSwitzerlandTel. +41 61 715 81 00Fax +41 61 715 25 00http://[email protected]

Combinable with

Accuracy (best possible accuracy)

10Basic

SensorD, L, W, P, H ±0.5%

50Standard

Sensor D, L, W, P, H

±0.5% Optional: ±0.2%

53High-end

Sensor W, P, H ±0.2%

51Custody transfer

Sensor W, P

±0.5% Optional: ±0.2%

23Two-wire

Sensor P, H ±0.5%

55Special applications

Sensor S, H ±0.2%

91 Basic

Sensor W

Onsite: <2.0% Under reference conditions: ±0.5%

93 High-end

Sensor W, P, C

Onsite: <2.0% Under reference conditions: ±0.5%

92 F Inline

Sensor F

Liquids For 2 or 3 beams: ±0.5%

For 4 beams: ±0.3%

93 T Portable

Sensor P

Onsite: <2.0% Under reference conditions: ±0.5%

Deltabar SPMD 70/75 Deltatop

Orifice plate DO: ±0.5 to 0.8%Pitot tube DP: ±1.0%

Nozzle DN: ±0.7 to 1.0%Venturi tube DV: ±0.7 to 1.0%

Deltabar MPMD 70/75 Deltatop

Orifice plate DO: ±0.5 to 0.8%Pitot tube DP: ±1.0%

Nozzle DN: ±0.7 to 1.0%Venturi tube DV: ±0.7 to 1.0%

Diameter

Elec

trom

agne

tic (

EMF)

Prol

ine

Prom

ag

Promag DWater/Waste water

DN 25 to 100 (1" to 4")

Promag LWater/Waste water

DN 50 to 300 (2" to 12")

Promag WWater/Waste water

DN 25 to 2200 (1" to 88")

Promag PChemical/Process applications

DN 15 to 600 (½" to 24")

Promag HHygiene

DN 2 to 100 (1/12" to 4")

Promag S Inhomogeneous fluidsHigh solid content

DN 15 to 600 (½" to 24")

Ultr

ason

ic

Prol

ine

Pros

onic

Flo

w

Prosonic Flow WClamp-on sensor Standard applications

DN 50 to 4000 (2" to 156")

Prosonic Flow WInsertion sensor Standard applications

DN 200 to 4000 (8" to 156")

Prosonic Flow PClamp-on sensor Process applications

DN 15 to 4000 (½" to 156")

Prosonic Flow CInline sensor Water/Waste water

DN 300 to 2000 (12" to 78")

Prosonic Flow FInline sensorTwo-wire technology

DN 25 to 150(1" to 6")

Diff

eren

tial p

ress

ure

Deltatop DOOrifice plate

DN 10 to 1000 (3/8" to 40")

Deltatop DPPitot tube

DN 40 to 12,000 (1½" to 480")

Deltatop DNNozzle

DN 50 to 500 (2" to 20")

Deltatop DVVenturi tube

DN 50 to 2000 (2" to 78")

Requirements Fluids (examples) Measuring principle

Elec

tro-

m

agne

tic

Cor

iolis

Ultr

ason

ic

Vort

ex

Ther

mal

Diff

eren

tial

pres

sure

Liqu

ids

Liquids in general Water • • • • •Flow rates < 2 l/h Additives, flavors • •Non-conductive liquids Oil, hydrocarbons • • • •Viscous liquids > 500 mPa�s Molasse, shower gel • •Cryogenic fluids Liquid O2 , Ar, N2 • • •Volume flow Water, milk, solvents • • • • •Mass flow Chemicals • • •Accuracy ≤ 0.2% • •Nominal pipe diameter DN > 500 • • •Operable flow range > 1:30 • • •Low pressure loss • • •Density, concentration, viscosity metering Foods, shower gel •Process temperature > 200 °C • • •

How to use this selection guide

Selecting the measuring principle

Define all the primary requirements for your measuring point: fluid type, nominal diameter, accuracy, pressure, temperature, etc.

In the table on Page 4, select the category for the type of fluid in question: Liquid – Gas – Steam – Special applications.

In the table, specify all the requirements (see Point )

you defined for your measuring point.

Now select the measuring principles to which all the

requirements apply (•).

Selecting the flowmeter

Now open out this brochure completely. The overview contains all the measuring principles you selected under Point and the corresponding Endress+Hauser flowmeters.

Now mark the sensors that can be installed in the pipe of your choice (DN = 1600 mm).

Mark those transmitters that can be combined with the

sensors in question and that meet the required accuracy specifications (<0.3% o.r.)

You have found the two flowmeters that suit your measuring point.

• Electromagnetic• Ultrasonic• Differential pressure

• Promag W• Prosonic Flow W (clamp-on)• Prosonic Flow W (insertion)• Prosonic Flow P• Prosonic Flow C• Deltatop DP• Deltatop DV

• 50 (W)• 53 (W)

• Promag 50W (standard)• Promag 53W (high-end)

Example

• Fluid: drinking water (urban area)• Pipe diameter: DN 1600• Required accuracy: <0.3% o.r.• Measured variable: Volume flow • Liquids

• Liquids in general • Volume flow• Nominal diameter DN > 500

• Electromagnetic• Ultrasonic• Differential pressure

2 3

➋ ➌ ➍

➎ ➏➑

Promag WWater/Waste water

➐ ➐➑

53High-end

50Standard

Requirements Fluids (examples) Measuring principle

Elec

tro-

m

agne

tic

Cor

iolis

Ultr

ason

ic

Vort

ex

Ther

mal

Diff

eren

tial

pres

sure

Liqu

ids

Liquids in general Water • • • • •Flow rates < 2 l/h Additives, flavors • •Non-conductive liquids Oil, hydrocarbons • • • •Viscous liquids > 500 mPa�s Molasse, shower gel • •Cryogenic fluids Liquid O2 , Ar, N2 • • •Volume flow Water, milk, solvents • • • • •Mass flow Chemicals • • •Accuracy ≤ 0.2% • •Nominal pipe diameter DN > 500 • • •Operable flow range > 1:30 • • •Low pressure loss • • •Density, concentration, viscosity metering Foods, shower gel •Process temperature > 200 °C • • •Process pressure > 100 bar Crude oil • • • •

Gas

Gas flow in general Natural gas, air • • • •Contaminated gas Biogas, exhaust gas • • •Volume flow Exhaust gas • •Mass flow CO2 • • • •Accuracy ≤ 0.5% Rare gas •Nominal pipe diameter DN > 300 • •Operable flow range > 1:30 • •Low pressure loss Air • •Process temperature > 200 °C Exhaust gas • •Process pressure > 100 bar CNG • • •

Stea

m

Volume flow • •Mass flow • •Nominal pipe diameter DN > 300 •Operable flow range > 1:10 •Low pressure loss •Process temperature > 300 °C Superheated steam • •Process pressure > 100 bar Superheated steam • •

Spec

ial

appl

icat

ions

Hygienic applications (SIP/CIP) Milk, beer • • •Slurries, suspended solids Thick sludge • •Liquid/liquid mixtures Oil/water, emulsions •Highly abrasive fluids (e.g. in mining) Ore slurry •Bidirectional metering (forward/reverse) • • • •Measurement from outside without process interruption/retrofitting/temporary metering •

Filling/bottling applicationsGas refueling applications

see Flow measurement OEM (inside)

Flow monitoring see Flow monitoring (inside)

Selection table “Measuring principles”

Please note:The selection table above provides a general overview and is used for quick clarification of suitable measuring principles. The table is not exhaustive. If further clarification is required, feel free to contact Endress+Hauser any time. We’ll be glad to be of assistance.

Supplementary documentation

4 5

Flow measurement For liquids, gases and steam

Products and services at a glance

FA005D/06/en(Order number 71024542)

Metering flow the cost- optimised way

Comprehensive metering point solutions for planning, commissio-ning and maintenance

CP006D/06/en(Order number 50109047)

Flow measurement in utilities

Energy management in your hands –customized solutions for compressed air, gas, steam and water

CP007D/06/en(Order number 71009419)

Flow handbook

A practical guide: Measurement technologies – applications – solutions

ISBN 3-9520220-4-7(Order number 50104766)

Precision for the real worldOur calibration facilities at your service

We calibrate your flowmeters on the world’s most advanced rigs – in our factory or onsite

CP010D/06/en(Order number 71091218)

Reduce energy costs

Tailor-made energy monitoring –rapid return on investmentFor steam, air, gas, oil, water, electricity, heating and cooling

CP014D/06/en(Order number 71109850)

Project documentation – data collection, archival, exportThe use of additional expansion mod-ules permits cost-saving administration and documentation of data for entire plant projects:• Clear presentation in a tree structure

of any desired number of metering points (e.g. by building, floor, meter-ing point), according to ISA 88.

• Uncomplicated inclusion of measur-ing devices directly from the Selection and Sizing functions. Also possible for instruments from other manufactur-ers or projects.

• Detailed listing of project manage-ment data (responsible person, cost-ing and budget data, etc.)

• Multiple data exchange possibilities in Excel or XML format: data export to other programs, data import from other projects, etc.

Applicator® • Optimal planning and

sizing of flowmeters• Administration and

documentation for entire plant projects

FieldCare® • Easy and dependable commissioning and

configuring of measuring devices via PC• Complete documentation of device settings• Storing device data (upload/download)• Simplified trouble-shooting

• Process-optimization through the visualization of measurement data in realtime (line plotting function)

• Analysis of diagnostic data for maintenance purposes• Administration and analysis of verification results

from the “Fieldcheck” test instrument

Fieldcheck® • Simulation and

testing of alarm/process conditions directly in the plant (without flow)

• Verification of flow-meters directly in the piping (without removal)

W@MApplicator ® – Optimal planning and sizingThe first steps are always the most important when it comes to planning metering points: An optimally dimensioned flowmeter at the right location provides many advantages. • Consistent process quality• Product savings due to error-free, precise measurement• Diminished risk of instrument failure at a later time

Proven over 20 years of useApplicator is a software for selecting and specifing flow- meters that has proven its abilities over many years. A wealth of industry experience and specialized know-how is embed-ded in Applicator. It enables people with limited technical knowledge to specify metering points quickly and easily.

The most recent version of Applicator has a raft of new features, including selection functions for all the other areas covered by Endress+Hauser – namely level, pressure, temperature, liquid analysis, etc. You’ll find that it opens up an enormous range of application possibilities in metrology and control.

Selection – straight to your objectiveWhen starting out to select the ideal flowmeter, Appli-cator guides you through all the important parameters. Just enter the type of fluid, required process data or metering point attributes and Applicator already displays the measuring principles and families of meters best suited to the case in hand.The Selection Tool contains over 600 products from all of the Endress+Hauser fields of operation.

Sizing – safe specificationBy entering further application-specific values, such as process pressure, process temperature or measuring range, Applicator immediately determines the ideal flowmeter type – and along with the suitable nomi-nal diameter, working range, pressure loss, accuracy, material loads, conformity with the Pressure Equipment Directives (PED) and corrosion resistance. Messages and warnings make it easy to select the right meter, help avoid common mistakes, and enable optimi-zation of the measuring point to suit specific require-ments. Additional Sizing Tools exist for level, pressure and energy measuring devices.

6 7

W@M – Life cycle management from Endress+ Hauser is an information system which provides tech-nical and operative management with complete data flow and archival – from commissioning on through

to maintenance and service within a plant, at any time or location. W@M is an open system based on Inter-net/intranet technology, and incorporating all software programs, products and services from Endress+Hauser.

Diameter Measuring range Pressure PN Processtemperature

Materials(wetted parts)

Process connection Protection Hygienic certification

Elec

trom

agne

tic (

EMF)

Prol

ine

Prom

ag

Promag DWater/Waste water

DN 25 to 100 (1" to 4")

0 to 10 m/s 0 to 600 m³/h

PN 16 Cl 150JIS 10 K

0 to +60 °C Polyamide liner Wafer: DIN, ANSI, JIS IP67 (NEMA 4X) –

Promag LWater/Waste water

DN 50 to 300 (2" to 12")

0 to 10 m/s 0 to 2400 m³/h

PN 10 to 16 Cl 150 –20 to +90 °C Polyurethane liner

PTFE liner Lap-joint flanges: DIN, ANSI IP67/IP68 (NEMA 4X/6P) –

Promag WWater/Waste water

DN 25 to 2200 (1" to 88")

0 to 10 m/s 0 to 136,000 m³/h

PN 6 to 40, Cl 150 to 300 JIS 10 to 20 K AWWA Class D

AS Table E, PN 16

–20 to +80 °C Hard rubber liner Polyurethane liner Flange: DIN, ANSI, JIS, AWWA, AS IP67/IP68

(NEMA 4X/6P) –

Promag PChemical/Process applications

DN 15 to 600 (½" to 24")

0 to 10 m/s 0 to 9600 m³/h

PN 10 to 40 Cl 150 to 300 JIS 10 to 20 K

AS Table E, PN 16

–40 to +180 °C PFA liner PTFE liner Flange: DIN, ANSI, JIS, AS IP67/IP68

(NEMA 4X/6P) –

Promag HHygiene

DN 2 to 100 (1/12" to 4")

0 to 10 m/s 0 to 282 m³/h

PN 16 to 40 Cl 150

JIS 10 to 20 K–20 to +150 °C PFA liner

Flange: DIN, ANSI, JIS, external thread, internal thread,

weld connection, clamp connection, couplings

IP67 (NEMA 4X) 3-A, EHEDG

Promag S Inhomogeneous fluidsHigh solid content

DN 15 to 600 (½" to 24")

0 to 10 m/s 0 to 9600 m³/h

PN 10 to 40 Cl 150 to 300 JIS 10 to 20 K

AS Table E, PN 16

–40 to +180 °CPTFE, PFA, polyurethane,

natural rubber liner,hard rubber liner

Flange: DIN, ANSI, JIS, AS IP67/IP68 (NEMA 4X/6P) –

Cor

iolis

Prol

ine

Prom

ass

Promass FUniversal flowmeter

DN 8 to 250 (3/8" to 10")

DN 25, 50, 80 (HT)0 to 2,200,000 kg/h

PN 16 to 100 Cl 150 to 600 JIS 10 to 63 K

–50 to +200 °C –50 to +350 °C (HT)

904L (1.4539)/ 316L (1.4404)

Alloy C-22 (2.4602)

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings, VCO

IP67 (NEMA 4X) 3-A, EHEDG

Promass MHigh pressure

DN 8 to 80 (3/8" to 3")

DN 8 to 25 (HP)0 to 180,000 kg/h

PN 40 to 100, PN 350 (HP) Cl 150 to 600 JIS 10 to 63 K

–50 to +150 °C DN 8...50: Titanium grade 9DN 80: Titanium grade 2

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings

IP67 (NEMA 4X) 3-A

Promass ALow flow rates

DN 1 to 4(1/24" to 5/32") 0 to 450 kg/h

PN 16 to 400 Cl 150 to 600 JIS 10 to 63 K

–50 to +200 °C 904L (1.4539) Alloy C-22 (2.4602) Tri-Clamp, VCO IP67

(NEMA 4X) 3-A, EHEDG

Promass IHygiene, viscosity

DN 8 to 80 (3/8" to 3") 0 to 180,000 kg/h

PN 40 to 100 Cl 150 to 600 JIS 10 to 63 K

–50 to +150 °C Measuring tube: Titanium grade 9Flange: Titanium grade 2

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings

IP67 (NEMA 4X) 3-A, EHEDG

Promass HChemically aggressive fluids

DN 8 to 50 (3/8" to 2") 0 to 70,000 kg/h

PN 40 Cl 150 to 300 JIS 10 to 20 K

–50 to +200 °C Zirconium 702/R 60702 Flange: DIN, ANSI, JIS IP67

(NEMA 4X) –

Promass EBasic applications

DN 8 to 80 (3/8" to 3") 0 to 70,000 kg/h

PN 40 to 100 Cl 150 to 600 JIS 10 to 63 K

–40 to +140 °C 904L (1.4539)316L (1.4404)

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings, VCO

IP67 (NEMA 4X) –

Promass ETwo-wire Basic applications

DN 8 to 50 (3/8" to 2") 0 to 70,000 kg/h

PN 40 to 100 Cl 150 to 600 JIS 10 to 63 K

–40 to +140 °C 904L (1.4539)316L (1.4404)

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings, VCO

IP66/IP67 (NEMA 4X) –

Promass S Food & Beverages

DN 8 to 50 (3/8" to 2") 0 to 70,000 kg/h

PN 40 to 63 Cl 150 to 300 JIS 10 to 40 K

–50 to +150 °C 904L (1.4539)316L (1.4435)

Flange: DIN, ANSI, JIS, Tri-Clamp, couplings

IP67 (NEMA 4X) 3-A, EHEDG

Promass PLife Sciences Industries(Pharma, biotechnology)

DN 8 to 50 (3/8" to 2") 0 to 70,000 kg/h

PN 40 to 63 Cl 150 to 300 JIS 20 to 40 K

–50 to +200 °C 316L (1.4435)Flange: DIN, ANSI, JIS,

Hygienic clamps, couplings and flanges

IP67 (NEMA 4X)

3-A, EHEDG,ASME BPE

Ultr

ason

ic

Prol

ine

Pros

onic

Flo

w

Prosonic Flow WClamp-on sensor Standard applications

DN 50 to 4000 (2" to 156")

0 to 15 m/s 0 to 678,550 m³/h

No limit Non-invasive –20 to +80 °C not wetted

(Clamp-on sensor) Clamp-on sensor IP67/IP68 (NEMA 4X/6P) –

Prosonic Flow WInsertion sensor Standard applications

DN 200 to 4000 (8" to 156")

0 to 15 m/s 0 to 678,550 m³/h PN 16 –20 to +80 °C 316L (1.4404) Welding connector IP68

(NEMA 6P) –

Prosonic Flow PClamp-on sensor Process applications

DN 15 to 4000 (½" to 156")

0 to 15 m/s 0 to 678,550 m³/h

No limit Non-invasive –40 to +170 °C not wetted

(Clamp-on sensor) Clamp-on sensor IP67/IP68 (NEMA 4X/6P) –

Prosonic Flow CInline sensor Water/Waste water

DN 300 to 2000 (12" to 78")

0 to 10 m/s 0 to 47,400 m³/h

PN 16 CI 150 –20 to +60 °C Carbon steel, epoxy coated Flange: DIN, ANSI, AWWA IP68

(NEMA 6P) –

Prosonic Flow FInline sensorTwo-wire

DN 25 to 150(1" to 6")

0 to 10 m/s 0 to 600 m³/h

PN 40CI 300 –40 to +150 °C

Meter body: CF3M (1.4404)Sensor: 316/316L (1.4404)

Flange: F316/F316L (1.4404)Flange: DIN, ANSI, JIS IP67/IP68

(NEMA 4X/6P) –

Vort

ex

Prol

ine

Prow

irl

Prowirl FFlanged version

DN 15 to 300 (½" to 12")

Liquids: 0.16 to 2360 m³/h Gases: 3 to 19,700 m³/h

PN 10 to 250 Cl 150 to 1500 JIS 10 to 40 K

–200 to +400 °COptional:

–200 to +450 °C

Meter body: CF3M (1.4404),Alloy C-22 (2.4602)

DSC sensor: 316L (1.4435), Inconel 718, Alloy C-22 (2.4602)

Flange: DIN, ANSI, JISOptional: with integrated reduction

of line size

IP67 (NEMA 4X) –

Prowirl WWafer version

DN 15 to 150 (½" to 6")

Liquids: 0.19 to 625 m³/h Gases: 4 to 5210 m³/h

PN 10 to 40 Cl 150 to 300 JIS 10 to 20 K

–200 to +400 °COptional:

–200 to +450 °C

Meter body: CF3M (1.4404)DSC sensor: 316L (1.4435) Wafer: DIN, ANSI, JIS IP67

(NEMA 4X) –

Ther

mal

Prol

ine

t-m

ass t-mass I

Insertion sensor DN 80 to 1500

(3" to 60") Gases: 0 to 120 m/s 290 psi g20 bar rel. –40 to +130 °C 316L (1.4404)

Alloy C-22 Thread: NPT, G1A IP67 –

t-mass FFlanged version

DN 15 to 100 (½" to 4") Gases: 0 to 120 m/s PN 16 to 40

Cl 150 to 300 –40 to +100 °C 316L (1.4404) Alloy C-22 Flange: DIN, ANSI, JIS IP67 –

Diff

eren

tial p

ress

ure

Deltatop DOOrifice plate

DN 10 to 1000 (3/8" to 40")

Liquids: 0 to 12 m/s Gases: 0 to 65 m/s Steam: 0 to 65 m/s

PN 6 to 420 Cl 150 to 2500 –200 to +1000 °C

C22.8 316Ti (1.4571)

15Mo3 (1.5415)

Wafer (corner tapping) Flange (flange tapping) Pipe unit (meter run)

IP68 (NEMA 6P) –

Deltatop DPPitot tube

DN 40 to 12,000 (1½" to 480")

Liquids: 0 to 12 m/s Gases: 0 to 65 m/s Steam: 0 to 65 m/s

PN 6 to 420 Cl 150 to 2500 –200 to +1000 °C C22.8

316Ti (1.4571)Cutting ring,

flange, flow tapIP68

(NEMA 6P) –

Deltatop DNNozzle

DN 50 to 500 (2" to 20")

Liquids: 0 to 12 m/s Gases: 0 to 65 m/s Steam: 0 to 65 m/s

PN 6 to 420 Cl 150 to 2500 –200 to +1000 °C

e.g. C22.8316Ti (1.4571)

15Mo3 (1.5415)13CrMo45

Flange: DIN, ANSI, JISWafer: DIN, ANSI, JIS

Butt-weld version

IP68 (NEMA 6P) –

Deltatop DVVenturi tube

DN 50 to 2000 (2" to 78")

Liquids: 0 to 12 m/s Gases: 0 to 65 m/s Steam: 0 to 65 m/s

PN 6 to 420 Cl 150 to 2500 –200 to +1000 °C

e.g. C22.8316Ti (1.4571)

15Mo3 (1.5415)13CrMo45

Flange: DIN, ANSI, JISWafer: DIN, ANSI, JIS

Butt-weld version

IP68 (NEMA 6P) –

EMF Dosimag

Filling/bottlingConductive liquids

DN 4, DN 8, DN 15K, DN 15

(5/32", 3/8", ½")

0 to 10 m/s0 to 1.66 l/s PN 16 –40 to +130 °C PFA liner Tri-Clamp, weld connection IP67

(NEMA 4X) 3-A, EHEDG

Cor

iolis

DosimassFilling/bottlingLiquids

DN 8, DN 15, DN 25

(3/8", ½", 1")

0 to 5 kg/s PN 40 –40 to +125 °C 904L (1.4539)316L (1.4404) Tri-Clamp, couplings IP67

(NEMA 4X) 3-A

CNGmassFuelingCompressed Natural Gas

DN 8, DN 15, DN 25

(3/8", ½", 1")0 to 150 kg/min max. 350 bar –50 to +125 °C 316L (1.4404)

316L (1.4435)

Internal thread: G½" (DN 8)G¾" (DN 15)G1" (DN 25)

IP67(NEMA 4X) –

CNGmass DCIFuelingCompressed Natural Gas

DN 8, DN 15, DN 25

(3/8", ½", 1")0 to 150 kg/min max. 350 bar –50 to +150 °C 316L (1.4404)

316L (1.4435)

Internal thread: G½" (DN 8)G¾" (DN 15)G1" (DN 25)

IP67(NEMA 4X) –

LPGmass FuelingLiquified Petroleum Gas

DN 8, DN 15, DN 25, DN 40

(3/8", ½", 1", 1½")0 to 70,000 kg/h

PN 40 Cl 150 to 300 JIS 10 to 63 K

–40 to +125 °C 316L (1.4404)904L (1.4539)

Flange: DIN, ANSI, JIS, VCO

IP67(NEMA 4X) –

CubemassLow flow rates

DN 1, DN 2, DN 4, DN 6

(1/24", 1/12", 5/32", ¼")0 to 1000 kg/h 160/400 bar –50 to +200 °C 904L (1.4539) VCO IP67

(NEMA 4X) –

Cubemass DCILow flow rates

DN 1, DN 2, DN 4, DN 6

(1/24", 1/12", 5/32", ¼")0 to 1000 kg/h 160/400 bar –50 to +200 °C 904L (1.4539) VCO IP67

(NEMA 4X) –

EMF Magphant

Limit switch/Trend displayConductive liquids

DN 1 to 2000(½" to 78") 0 to 5 m/s PN 16 –20 to +120 °C PVDF Weld nipple IP66

(NEMA 4X) –

Ther

mal

Flowphant DTT31Standard applicationsLiquids

DN 20 to 1000(3/4" to 40")

0.03 to 3 m/s as a relative value between

0 and 100%max. PN 100 –20 to +85 °C AISI 316L Weld nipple, compression fitting,

threaded connection: ANSI, ISO IP64 –

Flowphant DTT35Hygienic applications Liquids

DN 20 to 1000(3/4" to 40")

0.03 to 3 m/s as a relative value between

0 and 100%max. PN 100 –20 to +85 °C AISI 316L and FKM Viton,

EPDM (sealings)Conical metal-metal G½",

Tri-Clamp IP64 3-A

t-switch ATT11Limit switch Liquids, gases

DN 40 to 1000 (1½" to 40")

Liquids: 0 to 3 m/s Gases: 0 to 50 Nm/s PN 25 –10 to +80 °C 316L (1.4404/1.4435) Threaded connection: BSP, NPT,

couplings, Tri-ClampIP66

(NEMA 4X) –

t-trend ATT12Trend display Liquids, gases

DN 40 to 1000 (1½" to 40")

Liquids: 0 to 3 m/s Gases: 0 to 50 Nm/s PN 25 –10 to +80 °C 316L (1.4404/1.4435) Threaded connection: BSP, NPT,

couplings, Tri-ClampIP66

(NEMA 4X) –

Combinable with

Housings Display/Operation Ambienttemperature

Power supply Galvanic isolation Inputs Outputs Communication Accuracy (best possible accuracy)

Ex-approvals Protection

10Basic

SensorD, L, W, P, H

Compact AluRemote Alu

Two-line LCD/ push buttons

Operation via FieldCare–20 to +60 °C 85 to 250 V AC (45 to 65 Hz)

20 to 28 V AC (45 to 65 Hz) or 11 to 40 V DCElectronical connections are

galvanically isolated from each other – 4 to 20 mA, pulse/status HART® ±0.5% FM, CSA Div. 2 IP67 (NEMA 4X)

50Standard

Sensor D, L, W, P, H

Compact SSCompact AluRemote Alu

Two-line, backlit LCD/ push buttons

Operation via FieldCare

–20 to +60 °COptional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other Status 0/4 to 20 mA, pulse/frequency

(1 kHz passive), statusHART®, PROFIBUS PA,

PROFIBUS DP±0.5%

Optional: ±0.2% ATEX, IEC, FM, CSA, TIIS, NEPSI IP67 (NEMA 4X)

53High-end

Sensor W, P, H

Compact SSCompact AluRemote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare

–20 to +60 °C Optional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other

Status, current input

0/4 to 20 mA, pulse/frequency (10 kHz, active/passive), relays, status

HART®, PROFIBUS PA, PROFIBUS DP, FOUNDATION

Fieldbus, MODBUS® RS485±0.2% ATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

51Custody transfer

Sensor W, P

Compact AluRemote Alu

Two-line, backlit LCD/ push buttons

Operation via FieldCare–20 to +60 °C 85 to 260 V AC (45 to 65 Hz)

20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DCElectronical connections are

galvanically isolated from each other Status 0/4 to 20 mA, pulse/frequency (1 kHz passive), status HART® ±0.5%

Optional: ±0.2% ATEX, IEC IP67 (NEMA 4X)

23Two-wire

Sensor P, H Compact Alu

Four-line LCD/ touch control

Operation via FieldCare–20 to +60 °C

Two-wire12 to 30 V DC

13.9 to 30 V DC (Ex) (45 to 65 Hz)

Electronical connections are galvanically isolated from each other – 4 to 20 mA,

pulse/frequency, status HART® ±0.5% ATEX, FM, CSA IP67 (NEMA 4X)

55Special applications

Sensor S, H

Compact SS Compact AluRemote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare

–20 to +50 °COptional: –40 to +50 °C 20 to 260 V AC/DC (45 to 65 Hz) Electronical connections are

galvanically isolated from each otherStatus,

current input0/4 to 20 mA, pulse/frequency

(10 kHz, active/passive), relays, status

HART®, PROFIBUS PA, PROFIBUS DP,

FOUNDATION Fieldbus±0.2%

FM, CSA Div. 2 In preparation: ATEX II 3G,

IEC Zone 2

IP67 (NEMA 4X)

40 Basic

SensorE Compact Alu

Two-line, backlit LCD/ Operation via HART® resp.

FieldCare

–20 to +60 °C Optional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other Status 0/4 to 20 mA, frequency, status HART® Liquids: ±0.5%

Gases: ±1.0% ATEX, IEC, FM, CSA, TIIS, NEPSI IP67 (NEMA 4X)

80 Standard

Sensor F, M, A, I, H, E, S, P

Compact SSCompact AluRemote Alu

Two-line, backlit LCD/ push buttons

Operation via FieldCare

–20 to +60 °COptional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other Status 0/4 to 20 mA, pulse/frequency

(1 kHz passive), status HART®, PROFIBUS PALiquids: ±0.15%Optional: ±0.1%

Gases: ±0.35%ATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

83 High-end

Sensor F, M, A, I, H, E, S, P

Compact SSCompact AluRemote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare

–20 to +60 °C Optional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other

Status, current input

0/4 to 20 mA, pulse/frequency (10 kHz, active/passive), relays, status

HART®, PROFIBUS PA, PROFIBUS DP, FOUNDATION Fieldbus, MODBUS® RS485,

EtherNet/IP

Liquids: ±0.1%Optional: ±0.05%

Gases: ±0.35 %ATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

84 Custody transfer

Sensor F, M, A

Compact SS Compact AluRemote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare

–20 to +60 °COptional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other Status

0/4 to 20 mA, pulse/frequency (10 kHz, active/passive),

2 × pulse (90°/180°), relays, status

HART® MODBUS® RS485

Liquids: ±0.1%Gases: ±0.35 % ATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

TB2 Two-wire

Sensor E (two-wire)

Compact SS Compact Alu

Four-line LCD/ push buttons

Operation via FieldCare –40 to +60 °C Two-wire

18 to 30 V DCElectronical connections are

galvanically isolated from each other Status 4 to 20 mA, pulse/frequency, status HART®, PROFIBUS PA Liquids: ±0.25%

Gases: ±0.75 % ATEX, IEC, cCSAus IP66/IP67 (NEMA 4X)

91 Basic

Sensor W Remote Alu

Two-line LCD/ push buttons

Operation via FieldCare–20 to +60 °C 85 to 250 V AC (45 to 65 Hz)

20 to 28 V AC (45 to 65 Hz) or 11 to 40 V DCElectronical connections are

galvanically isolated from each other – 0/4 to 20 mA, pulse/status HART® Onsite: <2.0% Under reference conditions: ±0.5% FM, CSA Div. 2 IP67

(NEMA 4X)

93 High-end

Sensor W, P, C Remote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare

–20 to +60 °C Optional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other

Status, current input

0/4 to 20 mA, pulse/frequency (10 kHz, active/passive),

relays, status

HART®, PROFIBUS PA, PROFIBUS DP,

FOUNDATION Fieldbus

Onsite: <2.0% Under reference conditions: ±0.5% ATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

92 F Inline

Sensor F

Compact AluRemote Alu

Two-line LCD/ push buttons

Operation via FieldCare

Compact: –40 to +60 °CRemote: –40 to +80 °C

12 to 35 V DC, EEx i: 12 to 30 V DC, EEx d: 15 to 35 V DC

Electronical connections are galvanically isolated from each other – 4 to 20 mA, pulse/status HART®, PFM, PROFIBUS PA,

FOUNDATION Fieldbus

LiquidsFor 2 or 3 beams: ±0.5%

For 4 beams: ±0.3%

ATEX, IEC, FM, CSA, TIISIn preparation: NEPSI

IP67 (NEMA 4X)

93 T Portable

Sensor P Portable Plastic

Four-line, backlit LCD/ touch control

Operation via FieldCare0 to +60 °C Rechargeable battery + charger: 100 to 240 V AC

(47 to 63 Hz)Electronical connections are

galvanically isolated from each other 4 to 20 mA Data logger – Onsite: <2.0% Under reference conditions: ±0.5% – –

72 Standard

Sensor F, W

Compact AluRemote Alu

Two-line LCD/ push buttons

Operation via FieldCare

Compact: –40 to +70 °CRemote: –40 to +80 °C

Two-wire12 to 36 V DC,

EEx i: 12 to 30 V DC, EEx d: 15 to 36 V DC

Electronical connections are galvanically isolated from each other – 4 to 20 mA,

pulse/statusHART®, PFM, PROFIBUS PA,

FOUNDATION FieldbusLiquids: ±0.75% Volume

Gases/steam: ±1.0% Volume ATEX, IEC, FM, CSA, TIIS, NEPSI IP67 (NEMA 4X)

73 With flow computer

Sensor F, W

Compact AluRemote Alu

Two-line LCD/ push buttons

Operation via FieldCare

Compact: –40 to +70 °CRemote: –40 to +80 °C

Two-wire 12 to 36 V DC,

EEx i: 12 to 30 V DC, EEx d: 15 to 36 V DC

Electronical connections are galvanically isolated from each other

Pressure, temperature, density using HART®,

PROFIBUS PA, FF

4 to 20 mA, pulse/status,

frequency

HART®, PFM, PROFIBUS PA,FOUNDATION Fieldbus

Liquids: ±0.75% Volume, ±1% Mass Gases/steam: ±1.0% Volume

Gases/steam: ±1.7% MassATEX, IEC, FM, CSA, TIIS, NEPSI IP67

(NEMA 4X)

65 Standard

Sensor I, F

Compact AluRemote Alu

Two-line, backlit LCD/ push buttons

Operation via FieldCare

–20 to +60 °COptional: –40 to +60 °C

85 to 260 V AC (45 to 65 Hz) 20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DC

Electronical connections are galvanically isolated from each other 4 to 20 mA

0/4 to 20 mA, pulse/frequency (1 kHz, active/passive),

relays, status

HART®, PROFIBUS DP, MODBUS® RS485

Gases: ±1.5% o.r. (10% to 100% o.f.s.)±0.15% o.f.s. (1% to 10% o.f.s.)

ATEX, IEC, FM, CSA, NEPSI IP67

Deltabar SPMD 70/75 Deltatop

Compact SSRemote SS

Compact AluRemote Alu

Four-line LCD/push buttonsOperation via FieldCare –40 to +85 °C Two-wire

11.5 to 45 V DC No galvanic isolation – 4 to 20 mA HART®, PROFIBUS PA, FOUNDATION Fieldbus

Orifice plate DO: ±0.5 to 0.8%Pitot tube DP: ±1.0%

Nozzle DN: ±0.7 to 1.0%Venturi tube DV: ±0.7 to 1.0%

ATEX, IEC, FM, CSA, TIIS, NEPSI IP65

Deltabar MPMD 70/75 Deltatop Compact Alu

Remote Alu

Four-line LCD/push buttonsDIP switch

Operation via FieldCare–40 to +85 °C Two-wire

11.5 to 45 V DC No galvanic isolation – 4 to 20 mA HART®, PROFIBUS PA, FOUNDATION Fieldbus

Orifice plate DO: ±0.5 to 0.8%Pitot tube DP: ±1.0%

Nozzle DN: ±0.7 to 1.0%Venturi tube DV: ±0.7 to 1.0%

ATEX, IEC, FM, CSA, TIIS, NEPSI IP65

Compact version Compact SS Operation via FieldCare –20 to +60 °C 20 to 30 V DC Electronical connections are galvanically isolated from each other – Pulse, status – ±0.5%

Optional: ±0.25% – IP67(NEMA 4X)

Compact version Compact SS Operation via FieldCare –20 to +60 °C 20 to 30 V DC Electronical connections are galvanically isolated from each other – Pulse, status – ±0.15% ATEX II 3G IP67

(NEMA 4X)

Compact versionCustody transfer

Compact Alu Operation via FieldCare –40 to +60 °C 20 to 28 V AC 20 to 30 V DC

Electronical connections are galvanically isolated from each other – Pulse/frequency, status MODBUS® RS485 ±0.5% ATEX, IEC, FM, CSA

In preparation: TIIS, NEPSI IP67

(NEMA 4X)

Compact/remote versionCustody transfer

Compact SSCompact AluRemote Alu

Four-line, backlit LCD/ touch control

Operation via FieldCare–40 to +60 °C 85 to 260 V AC (45 to 65 Hz)

20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DCElectronical connections are

galvanically isolated from each other Status0/4 to 20 mA, pulse/frequency

(10 kHz, active/passive), 2 × pulse (90°/180°), relays, status

HART®, MODBUS® RS485 ±0,5% ATEX, CEC, NECIn preparation: NEPSI

IP67(NEMA 4X)

Compact versionCustody transfer

Compact Alu Operation via FieldCare –40 to +60 °C 20 to 28 V AC 20 to 30 V DC

Electronical connections are galvanically isolated from each other – Pulse/frequency, status MODBUS® RS485 ±0.2% ATEX, IEC, FM, CSA

In preparation: TIIS, NEPSIIP67

(NEMA 4X)

Compact version Compact Alu Operation via FieldCare –40 to +60 °C 20 to 28 V AC 10 to 30 V DC

Electronical connections are galvanically isolated from each other – 4 to 20 mA, pulse/frequency MODBUS® RS485 ±0,1% ATEX, IEC, CEC, NEC

In preparation: TIIS, NEPSIIP67

(NEMA 4X)

Compact/remote versionRemote SS

Compact AluRemote Alu

Two-line, backlit LCD/ touch control

Operation via FieldCare–40 to +60 °C 85 to 260 V AC (45 to 65 Hz)

20 to 55 V AC (45 to 65 Hz) or 16 to 62 V DCElectronical connections are

galvanically isolated from each other Status 4 to 20 mA, pulse/frequency MODBUS® RS485 ±0,1% ATEX, IEC, CEC, NECIn preparation: TIIS, NEPSI

IP67(NEMA 4X)

Compact version Compact Alu LED –20 to +60 °C 20 to 30 V DC No galvanic isolation – 4 to 20 mA, relays – ±2.0% FM, CSA Div. 2 IP66(NEMA 4X)

Compact version Compact SSOne-line, backlit LCD –

Color change on faults, LED’s for status indication, push buttons

–40 to +85 °C 18 to 30 V DC (reverse polarity protection) No galvanic isolation –

1× or 2 × PNP switching outputs,optional: 1× PNP switching output and 1× 4 to 20 mA output, active

Programmable by a PC(ReadWin® 2000 and FieldCare) ±2.0% – IP64

Compact version Compact SSOne-line, backlit LCD –

Color change on faults, LED’s for status indication, push buttons

–40 to +85 °C 18 to 30 V DC (reverse polarity protection) No galvanic isolation –

1× or 2 × PNP switching outputs,optional: 1× PNP switching output and 1× 4 to 20 mA output, active

Programmable by a PC(ReadWin® 2000 and FieldCare) ±2.0% – IP64

Compact version Compact SSCompact Alu

LED, 4-digits, LCD (option)DIL switches

–10 to +65 °C without LCD 18 to 30 V AC/DC No galvanic isolation – Relays – ±5.0% – IP66

Compact version Compact SSCompact Alu

LED, 4-digits, LCD (option) push buttons

–10 to +65 °C without LCD 18 to 30 V AC/DC No galvanic isolation – 4 to 20 mA, open collector – ±5.0% – IP66

Flow measurement

Subj

ect t

o m

odifi

catio

n

Flow measurement OEM

Flow monitoring

TransmittersSensors