To tackle the complicated problem of filter planning for a residential feeder,
primarily, it can be subdivided to the followings:
1. Basically, each filter is tuned to a harmonic order. The main aim is to
provide a system-wide mitigation of that harmonic order. The main
question is how many filters are needed and where they have to be
placed?
Figures below show how a single filter location in a very simple feeder
affects the system-wide harmonic distortion indices:
2. Then, one has to verify that the planned filters are avoided to introduce
any magnitude amplification of other harmonic orders in the system. The
undesired harmonic increase may happen by a parallel resonance in the
system. Methodologies have to be developed to address the issue.
Substation
A block of residential loads
(e.g. a neighbourhood)
Filt
er
Normal Harmonic flow
New harmonic flows
after the filter is installed
Harmonic Filters For Residntial Feeders
Pooya Bagheri M.Sc. Department of Electrical and Computer Engineering, University of Alberta
Nowadays, the rapid growth of nonlinear electronic home appliances
has resulted in significant voltage and current waveform distortions in
residential distribution systems. Although each of the consumer
electronic devices is not individually a big source of harmonics, the
collective effect will be considerable and can become a serious concern
of utility companies.
Hence, there is an essential need of research for effective harmonic
filter planning strategies in residential distribution systems.
Introduction
Modern vs. Traditional Harmonic Problems
Power and Energy Innovation Forum ♦ University of Alberta ♦ November 2011
The Proposed Research
Supply System
Filt
er
Industrial H-source
loadsThe transformer impedance
avoids attraction of system
harmonics toward the filter
The 240/25 kV
Substation
Downstream
loads
Upstream
loads
Filter 1
Telephone line
sections
Filter 2
(if necessary)
Monitoring
Location
F1
F2
C
A
B
C
N
3C/a2
1:a Trans. Series
impedance
Open Circuit
Equivalent Zero-Seq
Circuit
Equivalent Pos/Neg-Seq
Circuit
Industrial Plants (the traditional harmonic problem):
Residential Feeders (The modern harmonic problem):
The following issues make the filter planning methods required for the
residential feeders totally different (and more complicated) from the traditional
methods usually applied to industrial harmonic problems:
• Harmonic sources are not big loads concentrated in one location (like the
industrial ones). There are several small sources dispersed through all the
network. Therefore, the filter location to achieve a system-wide harmonic
mitigation is not anymore obvious.
• There is no transformer associated impedance (like the one in industrial
plants). A filter can attract the upstream harmonics which may be even
causing higher distortions in some segments of the system.
•Harmonic resonance analysis will not be as simple as the methods used in
an industrial plant filter design.
Zero-Sequence Filter Design for a Real Telephone Interference Problem
• Since a system-wide harmonic reduction is not essential for a telephone interference problem mitigation, the
required filter placement is not too complicated. The only issue is about undesired attraction of upstream
harmonics by the installed filter. For this project, this issue is investigated by some analytical and simulation
studies and it was verified that for this specific feeder, it is not problematic and one filter was found to be
sufficient.
• The 9th harmonic was identified as the main contributor to the interference problem. Hence, the filter was tuned
to this harmonic order.
• As the main privilege of zero-sequence filters, they appear as open-circuit for equivalent nonzero-sequence
circuits and consequently do not have any effect on the pos/neg-sequence harmonics. Therefore, there is no
concern of possible parallel resonance in the other harmonics caused by such filters installation!
• During the project it was revealed that present analytical (such as k-factor) indices are not sufficient for such
filters loading assessment. Hence, a new methodology was developed to evaluate the filter overloading.
3rd 5th 7th 9th 11th 13th 15th0
2
4
6
IDD
(%)
Harmonic order
No Filter
One Filter installed at location F1
Two Filters installed at both locations (F1 & F2)
1st 3rd 5th 7th 9th 11th 13th 15th Total rms0
50
100
150
Ind
uce
d V
olt
age(V
)
Harmonic order
No Filter
One Filter installed at location F1
Two Filters installed at both locations (F1 & F2)
The Zero-Sequence Filter Schematic
0 10 20 30 40 50 60 70 80 90 1000
0.5
1
Filter location: x (% of feeder length)
Sca
led
to
Maxim
um
Average Voltage THD
Average Current THD
Sub.
Fx