Feeder Neutral Potential Rise
Due to GPR Transfer and Induction
ATCO Electric
Presented by Alex Nassif at the
APIC Power & Energy Innovation Forum – 2014
University of Alberta, ETLC Solarium
5 November 2014
2 Confidential – all rights reserved
144 kV
Substation
MGN
25 kV Transmission side
Distribution side Customer side
gnR
nZ
nZnZnZnZ
subRgnR gnRgnRgnR
///
Equivalent circuit of Upstream ends
Problem Definition
Should the substation neutral be connected to the feeder neutral?
MGN ONLY
3 Confidential – all rights reserved
Problem Definition
For a long time ATCO and other utilities had no answer to the
question
1990’s – many questions raised
More prevalent in underground cables emanating out of the
substation
‒ Should the substation end of the cable be left disconnected?
‒ Should the riser pole end of the cable be left disconnected?
‒ Should both be connected?
‒ With current flowing through the underground cable neutrals will the
cable ampacity be reduced?
‒ Should an arrestor be used for bonding the neutral to the substation
ground?
144 kV
Substation
MGN
25 kV Transmission side
Distribution side Customer side
gnR
nZ
nZnZ
nZ
nZ
subRgnR gnRgnRgnR
///
Equivalent circuit of Upstream ends
U/G
4 Confidential – all rights reserved
Problem Definition
2012 – ATCO took a more active role in seeking out answers
Other AB utilities also had questions.
Fortis AB example:
‒ Prior to 2008 – Earth Return system in rural areas
‒ MGN required in urban areas – communication joint use of poles
‒ After the 2006 analysis by Dr. Xu, Fortis decided to introduce more MGN
systems (helps telephone interference too)
5 Confidential – all rights reserved
Problem Definition
Substation GPR can be transferred and cause NPR
‒ How bad is the resulting NPR?
What are the implications of not connecting?
‒ This represents a broken neutral configuration.
6 Confidential – all rights reserved
Problem Definition
This project was initiated to try and address these issues.
To ATCO Electric and other AB utilities safety is paramount.
Next slides show the developments, results and conclusions of the
APIC study.
7 Confidential – all rights reserved
GPR Transfer – Distribution or Transmission?
Equivalent voltage source of GPR Fault current flow pattern in substation
Fault inside substation Fault outside substation
8 Confidential – all rights reserved
Substation GPR Transfer
faultsubsubstation IRGPR
Propagation of GPR from the substation to the system:
substation
n
MGNn
MGNneutral GPR
ZZ
ZNPR
sRZZ gnMGN
Transfer ratio
0
2
4
6
8
10
12
14
16
0 0.5 1 1.5 2Neutral length [km]
Equiv
lent im
ped. [o
hm
]
Z’geq
9 Confidential – all rights reserved
Substation GPR Transfer - Results
GPR transfer ratio
substation
n
MGNn
MGNneutral GPR
ZZ
ZNPR
Transfer ratio
10 Confidential – all rights reserved
Substation GPR Transfer - Results
Observation GPR transfer ratio k
Max NPR per kA (V/kA)
Corresponding system condition
High end value 0.95 129 m 50S, 30 gnR
Typical value 0.91 124 m 001S, 15 gnR
Low end value 0.76 108 m 500S, 7 gnR
NPR – neutral potential rise = GPRneutral
Notice how high this can get
11 Confidential – all rights reserved
Substation GPR Transfer - Results
gnRgnRgnRgnR
nZ nnZnZ
nZ nZ nZ
maxNPR
GPRgnR
Customer #1 Customer #2
2NPR NNPR
Neutral voltage rise (NPR) at customer locations
1 maxNPR =NPR =k×GPR2 1 1NPR =k ×NPR i+1 i iNPR =k ×NPR
n
nNPR =k ×GPR
…..
Corresponding system condition
Max NPR per kA
NPR per kA at 2 km (V/kA)
NPR per kA at 5 km (V/kA)
m 50S, 30 gnR 129 24 3.4
m 001S, 15 gnR 124 22 3.2
m 500S, 7 gnR 108 46.4 12
Noticeably lower as distance increases
12 Confidential – all rights reserved
Induction caused NPR
X N totalGPR I Z
|GPR|
Net GPR profile
Islanded neutral
I
I
Neutral V = Neutral GPR
Will the GPR close to the first pole become unacceptably high if the neutral is not connected?
13 Confidential – all rights reserved
Induction caused NPR
Induced voltages in the neutral during a LG fault Conversion of voltage sources to current sources
Series connection of individual current sources Shunt current sources at locations of peak NPRs
14 Confidential – all rights reserved
Induction caused NPR
Parallel Zone
NPR caused by
source at F
NPR caused by source at X
Net NPR profile
Neutral exposure
with fault current
X F
Neutr
al V
|N
eutr
al V
|
IF
znn
RgnRgn Rgn Rgn Rgn RgnRgn
znn znn znn znn znnen en en
+ - + - + -
X YF
15 Confidential – all rights reserved
Induction caused NPR
A typical value of Ztransfer for distribution lines in AB is about 0.34 ohm (s = 1km).
For example if a fault current is 1kA, the maximum GPR is 340 V.
NPR profile due to two shunt current sources
1
2
mF nn gn F
nn
ZNPR Z R s I
Z
maxm
nn gn F
nn
ZNPR Z R s I
Z
Absolute value of NPR profile
Ztransfer Ztransfer
16 Confidential – all rights reserved
Induction caused NPR
Case study
NPRmax for different fault locations NPR profile for fault at 6 km from substation
17 Confidential – all rights reserved
Substation GPR Transfer vs Induction
If neutrals are not connected:
Observation GPR transfer ratio k
Max NPR per kA (V/kA)
Corresponding system condition
High end value 0.95 129 m 50S, 30 gnR
Typical value 0.91 124 m 001S, 15 gnR
Low end value 0.76 108 m 500S, 7 gnR
There may be a concern
(Note that the fault currents
are different)
NPRmax=0.124IF_1
NPRmax= Ztransfer IF_2 = 0.34 IF_2
18 Confidential – all rights reserved
Substation GPR Transfer vs Induction
GPR transfer & inductive coupling effects
Summary: more investigations are needed to find the best compromise
19 Confidential – all rights reserved
APIC Report Conclusions
The NPR is caused by substation GPR transfer and inductive coupling.
If the neutral is not connected:
‒ The substation GPR is not transferred to the MGN.
‒ Induction coupling effect is highest close to the substation.
If the neutral is connected:
‒ The GPR transfer is the worst and NPR is highest in the first few grounding
structures.
‒ Induction is greatly reduced close to the substation
Therefore, it can be said that the GPR transfer and induction have conflicting
requirements
20 Confidential – all rights reserved
ATCO’s Direction
Ground potential
No. of grounding points
from substation
Substation neutral
First grounding point outside fence
(neutral connection point)
600V threshold
Hazard zone
Should not happen in public area
i.e. if it happens in a public area,
NPR is too dangerous
21 Confidential – all rights reserved
ATCO’s Direction
Why 600V threshold?
V0
0.5m
Step Voltage
V0
V0 is the NPR
0.116body
s
It
0.1161000step
s
Vt
IEEE Std.80 (t=0.5s) Simplified (t=0.5s)
50 kg 726.0 V 453.8 V
70 kg 982.6 V 614.1 V
Rod=1.5m
22 Confidential – all rights reserved
ATCO’s Direction
Is the feeder O/H or U/G?
O/H
Is there a M.G.N on the riser pole?
Does the O/H line have a neutral leaving the
substation?
Is the pole located in an area frequently travelled
by the public?
Connecting the concentric neutral to the substation ground is recommended
Connect; Refer to isolation
manual
Not a Concern
U/G
Next Slide
23 Confidential – all rights reserved
ATCO’s Direction
Connecting the neutral to the substation ground is
recommended Fault level (amps)
Substation grounding resistance
Cable Leaving the Substation
System Neutral or U/G system Cable
Are the first X grounding points
(Ground Rods, Pull Boxes, etc.)
located in areas frequently
travelled by the public?
Connect; Refer to isolation
manual YES ….
Data for Calculation
Previous Slide
24 Confidential – all rights reserved
ATCO’s Direction
Some perceived additional benefits of connecting:
‒ Reduction in GPR at the fault point for a feeder fault (smaller equivalent
impedance).
‒ Reduction in interconnected ground impedance, helping protective devices
operate properly under high impedance fault conditions.
‒ Reduction of induced voltage closer to the substation due to feeder faults.
‒ Added safety to personnel by eliminating potential difference between MGN
and the concentric neutral at the riser pole where connection is made.
‒ Reduction in telephone interference (IT) with telephone buried service close to
the substation.
‒ Reduction in uncontrolled stray current traveling through earth return. These
can be harmful to both animals and humans.
25 Confidential – all rights reserved
ATCO’s Direction
Issues of connecting:
‒ Transferred GPR for a fault at the substation.
‒ Cable ampacity reduction, which may require de-rating.
‒ Increase in single-line to ground fault levels (positive or negative?).
‒ Increase in neutral voltages at customer sites during a fault.
26 Confidential – all rights reserved
ATCO’s Direction
Risk-benefit (HAZCOM) analysis:
‒ Faults inside the substation are rare and clearing time is very short.
Equipment failure and animal contact are the main reasons.
‒ The problem of NPR due to GPR transfer is not being introduced with
the connection. Only the likelihood is increased.
‒ What damage/safety concern can we expect from NPR?
‒ The likelihood of safety risks or damage is higher for faults outside the
substation and induction is the main concern. Lightning-related faults
are very common and the main reason for a fault on the line.
ATCO has established a process to connect the neutral to the
substation grounding grid and properly isolate dangerous
structures from the public, where needed.